corbinoni
Member
- Location
- Twin Cities,Minnesota
The question reads:A panelboard supplied by a transformer A)a set of fuses overcurrent protection determined by multiplying the secondary conductor ampacity by the secondary to primary transformer voltage ratio.B)Overcurrent protection on the secondary side of the transformer not greater than the panelboard rating.C)inherent thermal protection of the transformer.D)6 sets of fuses having combined rating not greater than the panelboard rating. I read 408.36 B and decided B to be my primary selection but do you think anything else makes any sense.I do know that from 450.3 theres conditions that allow the protection to be on the primary of the transformer.