I was told recently by a manufacturer rep. that most 3ph transformers (excluding power transformers) are only really loaded to 35%? I found this to be a very interesting statistic, he also told me that this is kind of the reason why most manufacturers are trying to maximise transformer efficiency at 35%.
I understand that most of the time the load calc is done based on connected load-and obviously the demand factor is applied, but this statistic seem to suggest that most transformers are oversized?
Another interesting thing I was told was that to obtain UL listing for his manufacturer (they are just starting out in the industry), one of the tests they did was run 200% load for 30mins and if it doesnt blow up - its all good.
I understand that most of the time the load calc is done based on connected load-and obviously the demand factor is applied, but this statistic seem to suggest that most transformers are oversized?
Another interesting thing I was told was that to obtain UL listing for his manufacturer (they are just starting out in the industry), one of the tests they did was run 200% load for 30mins and if it doesnt blow up - its all good.