There are two basic sources of KW flow to a motor operating at 'no load'. One is electrical losses expressed as load or copper losses, core losses, parasitic losses including stray flux. The mechanical losses consist of windage and friction. Windage losses follow the fan curves for the style of fan employed. Friction losses depend on the bearing system employed and RPM. Total losses at NL are typically less than half of FL losses. Electrical losses are the majority of the FL Loss number. If the motor is 94.3% Eff, the total losses are 100% - 94.3% = 5.7% . 93.5-95.5% is a typical efficiency for motors in the NLA range which you suggest. 100NLA or so implies 200-250HP @460V. 460V systems are typically 60Hz, implying 1800RPM. The same motor typically will operate on a 380V/50Hz system at 1500RPM, with a HP reduction proportionate to the reduction in RPM or applied Hz. This assumes adequate core for 50 HZ operation. Some deration is required if core losses are elevated due to Hz reduction.
In general terms, windage is reduced according to the fan curves, friction roughly proportionately to speed, and electrical losses proportionately to current reduction.
On a typical V/Hz drive, the output voltage is reduced proportionately to Hz, so at say half speed, half voltage is applied. Half voltage at constant current is roughly half power, assuming PF remains constant. One can simply read the NLA off of the drive at various frequencies and estimate KW flow. Most drives will also display KW, so one could adjust the speed as desired and directly read KW flow from the drive display at the desired speeds.