renosteinke
- NE Arkansas
I can't agree with that.
Here's why: Look to any UL standard, and you'll find that were circuits are required to be class 2 or class 3, there are many other requirements. After all, it's possible to use too large of a class 2 transformer - that is, to use a transformer that is capable of providing enough power to create the hazard you're trying to avoid. It's kind of like saying an ordinary circuit is 'limited' simply because there's a fuse on it.
Which, incidentaly, is the real reason for 'power limited' transformers. By having the transformers' impedence limit the power available, the circuit designers are able to avoid using a fuse that UL would otherwise require. This is a matter completely apart from whether the power is limited so as to prevent another hazard (for example, an intrinsically safe circuit).
Now, I don't expect anyone to take my explanation here at face value. Chat with your UL guys, review a few UL standards - I might suggest the ones describing fire alarm control panels would be a good place to start - and you'll see what I mean.
Here's the short version of the testing procedure:
The transformer is shorted out.
If it has a fuse, the fuse has to blow- and, btw, the transformer is not allowed to get hot.
If there is no fuse, the transformer has to exceed a certain temperature, to 'prove' that it is preventing excess power from entering the circuit. It HAS to get hot.
I think we can all see the many reasons a manufacturer might want to do away with the fuse - and most of them have nothing to do with the nature of the control circuit.