liquidtite
 - Ny
why dont they make a 4 wire assemble for nm12/4 w/ground MC is a staple of mine. Makes life real easy.
even if the load is unbalanced isnt that the reason why you would make shure all hots are on seperate phases so it would cancel out the load on the nuetralOn a ballanced linear circutuits the neutral load would be 0
With non-linear loads the neutral load would be the triplen harmonics.
I really don't know if that would be worse or not with 2 loaded legs or 3.
Not if their magnitudes are similar and phase angles consistent with the 3-phase primary, no. Harmonics are no different that any other signal. They will cancel if they are all the same, and fall within the 0, 120, 240-degree triangle. If they are unbalanced, then they will not cancel. The only time you will have a problem is when there is a signal manipulation on 1 phase but not the others. If all three phases are manipulated in the same manner, then all three manipulations will negate one another.
whats a nonlinear load a mwbc?No, no chance assuming wired correctly.
If you loaded up all three circuits to 20 amps of non-linear load you might have more than 20 amps on the neutral.
But would you design a circuit like that?
I agree. I see nothing wrong with Bob's posts.I'm' sure Bob wouldn't but, I advise you to get off your high horse. It is apparent that you are daring us as well as continuing to be abusive to a number of members.
Roger
Check again Rick. Triplen harmonics add in the neutral of a three-phase system.Not if their magnitudes are similar and phase angles consistent with the 3-phase primary, no. Harmonics are no different that any other signal. They will cancel if they are all the same, and fall within the 0, 120, 240-degree triangle. If they are unbalanced, then they will not cancel. The only time you will have a problem is when there is a signal manipulation on 1 phase but not the others. If all three phases are manipulated in the same manner, then all three manipulations will negate one another.
You are correct, of course. Much discussion can be found on the additive problem with triplen harmonics.Third multiple harmonics are additive and do not cancel
Well he could use the same font as Charlie B. that is so easy for those of us over forty to read, but as far as content; no complaints from me.I agree. I see nothing wrong with Bob's posts.
thanks im familiar with mwbcs but havnt heard of linear loads thanks for the infoAn example of non linear loads is flourescent lights, computers, copiers and such.
MWBC = multiwire branch circuit, 2 or 3 hots(different poles/phases) with 1 neutral.
what is a harmonic load?Not if their magnitudes are similar and phase angles consistent with the 3-phase primary, no. Harmonics are no different that any other signal. They will cancel if they are all the same, and fall within the 0, 120, 240-degree triangle. If they are unbalanced, then they will not cancel. The only time you will have a problem is when there is a signal manipulation on 1 phase but not the others. If all three phases are manipulated in the same manner, then all three manipulations will negate one another.
One which the load's current has multiples of the fundamental frequency. For example, 120 and 180Hz are second and third harmonic currents of a 60Hz fundamental frequency.what is a harmonic load?
Say you have a balanced mwbc with identical loads and excessive triplen harmonics such that there was 10A on all 4 wires. That means each leg is contributing 33% to the neutral current (so 67% fundamental). Turn off one leg and the neutral will see 67% fundamental plus 2 times 33%, which amounts to 13.3A of current on the neutral.On a ballanced linear circutuits the neutral load would be 0
Check again Rick. Triplen harmonics add in the neutral of a three-phase system.Ok, I guess I am in over my head... I was taught that 60 Hz, along with 120 and 240 even multiple harmonics cancel. Third multiple harmonics are additive and do not cancel, and will cause the largest distortion of wave forms
Surely,with 3 loaded legs,the neutral load of 3rd harmonics is worse than with 2 loaded legs because the 3rd harmonics in each phase are in phase.
This is not correct, and is actually quite common with single phase loads on a 3-phase system. If you have a motor load on the B-phase and a resistive load on the C-phase, then your neutral current will exceed the ampacity of the neutral. (Forgive me if I have my leading/lagging backward, but the principle is the same.) This is the biggest reason for burning up neutrals in power distribution systems and MWBC's.
What is even harder to comprehend for many, is that if you simply reverse the phases, then the current in the neutral will be reduced for the same loads. This is a situation where phase rotation is important.
No. Anything that is balanced will still cancel, including the harmonics. The wording in the NEC is rather poor in this area because it causes people to overlook powerfactor. I don't recall the actual wording at this time, but my recollection of it is that it is misleading because it "suggests" that powerfactor is not part of the issue, when in fact, it is the major contributor to the problem.
P.S. Just for reference, here is the same diagram I used recently for another discussion. It is the same diagram, except it is based on resistive loads.
Thanks was looking for a answer like that.