I don't know of any reason you couldn't run the gec in with the feeder as long as the gec is not a solid conductor and any bonding is done where it is required.
Why can't the GEC be a solid conductor?
I thought 310.3 did not apply to GECs because of 250.62.
Where in 250.62 does it state that the solid gec is allowed in a raceway. It states the gec may be solid but I don't see that as permission to install it in a raceway.Why can't the GEC be a solid conductor?
(C) Stranded Conductors. Where installed in raceways, conductors 8 AWG and larger, not specifically permitted or required elsewhere in this Code to be solid, shall be stranded.
Good luck pulling it in a conduit.
250 does not say you cannot but 310 does say you cannot unless it is specifically allowed elsewhere. Show me where 250 says you can install a solid gec in a raceway.Where does it say I cannot? The exception seems to allow it.
A sleeve is not a raceway and it still does not say if it is solid it can be in a raceway. If it indeed said a GEC could be installed in a raceway that, IMO would not include the solid wire unless it specifically stated that. 310 is still there. Circuit conductors may be solid or stranded but we know that we cannot install them in a raceway
Well if that is the case, I still do not see an exception to allow solid in the conduit. If you choose to use solid then don't sleeve it. If you must sleeve it then use stranded. Again I think the definition of raceway does not mean a sleeve. A sleeve is not an enclosed channel. When it enters a jb or enclosure the raceway is enclosed.
Anyway you look at it in the OP's situation I don't think a solid wire would be used and quite frankly I don't see an issue if the raceway was just be used with the egc. When other conductors are there I think that could cause problems.
I will agree that the code is not perfectly clear on this but....