Could you describe it differently.
Sorry I meant angle or U pull. Sounds like a U pull in which case Gus is correct.Angle pull.
It sounds like 48 conduits entering on one side of a box.
Sounds like 48 entering the bottom to me.Sounds to me like 24 entering the bottom. The question is are they leaving via the top (opposite of entry) or the side of the box?
The distance between raceway entries enclosing the
same conductor shall not be less than six times the metric
designator (trade size) of the larger raceway.
24 - 2" conduits through the floor entering top of junction box, 6 conduits across 4 deep.
24 - 2" conduits out side of junction box, 6 conduits across 4 high.
Part of 314.28(A)(2)