dedicated = individual ? ...as in one hot and one neutral per circuit. If so, these neutrals always count, regardless of other issues.Since they are 20 dedicated nonlinar loads circuits, the neutrals should not be considered current carring conductor. That would mean only 20 current carring conductors in raceway and no derating nessary, is that correct.
Much thanks Dennis Alwon, augie47 and Smart$ It looks like some larger wire needs to be pulled for these 20 amp recepticals.
I don't believe installing a divider will magically make one wireway qualify as two... :happysad:it might be cheaper to just put a divider downt he center of the raceway and split it into two chunks.
Even if the neutral did count, the overall count would drop: 20? + 7N = 27CCC. Code compliant with breaker handle ties. Meets spec's and other non-NEC issues???If you used a common neutral with 3 conductors on different phases then you would not count the neutral unless this is fluorescent lighting or computer type loads(non linear)
Perhaps separate(d) raceways... but the ampacity requirement is for the "wireway", not per "raceway".why wouldn't it? it is two seperate places for wires to run.
it is listed that way for seperating different voltage levels of conductors, so it has to be seperate raceways.