125C supply conductors

Status
Not open for further replies.
I saw some HID's the other day that required 125C supply conductors. Isn't that rather uncommon?

That's a new one one me.

Anything over 90C is 'special applications'. See 310.13(A)'s table. Where are you supposed to get FEP, PFA, SA, Z or ZW? Your only other choice is MI and that would seem to be overkill for lights, plus being a bit dicey to connect.

Also, there are no 125C conductors. It looks like it jumps from 90 to 150.
 
Last edited:
That's a new one one me.

Anything over 90C is 'special applications'. See 310.13(A)'s table. Where are you supposed to get FEP, PFA, SA, Z or ZW? Your only other choice is MI and that would seem to be overkill for lights, plus being a bit dicey to connect.

Also, there are no 125C conductors. It looks like it jumps from 90 to 150.

Here ya go......
 