ASG

Senior Member
Location
Work in NYC
Occupation
Electrical Engineer, PE
I was reading this old thread and it said 4 wires to the building is required. Where does it say this? I am running a feed for a mechanical equipment panel and was not planning on running a neutral.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If you have no line to neutral loads, there is no code rule that says you have to run the neutral to the second building. You are required to install an EGC with the ungrounded conductors.
 

pete m.

Senior Member
Location
Ohio
I was reading this old thread and it said 4 wires to the building is required. Where does it say this? I am running a feed for a mechanical equipment panel and was not planning on running a neutral.

Is there already a feeder for lighting and receptacle loads? Maybe take a look at 225.30 and make sure you are in compliance.

Pete
 

ASG

Senior Member
Location
Work in NYC
Occupation
Electrical Engineer, PE
Is there already a feeder for lighting and receptacle loads? Maybe take a look at 225.30 and make sure you are in compliance.

Pete

Yes, this is a hospital where we are feeding a new Emergency Mechanical Equipment panel.
 

pete m.

Senior Member
Location
Ohio
Then it would seem 225.30(A)(2) would allow the additional feeder as long it is classified as "emergency" i.g. essential to the preservation of human life.

Pete
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Then it would seem 225.30(A)(2) would allow the additional feeder as long it is classified as "emergency" i.g. essential to the preservation of human life.

Pete
Even if it is not an emergency circuit or even a legally required stand by circuit, 225.30(A)(4) would permit it.
 

ASG

Senior Member
Location
Work in NYC
Occupation
Electrical Engineer, PE
Little wrinkle: the panel I'm installing is being fed from a transformer. To meet 240.21(C), we installed a main disconnect within 10 feet of the transformer on the secondary side. Now, since this panel is installed in a different building, it will also require a main. How do we do this without creating coordination issues?
 

jumper

Senior Member
Little wrinkle: the panel I'm installing is being fed from a transformer. To meet 240.21(C), we installed a main disconnect within 10 feet of the transformer on the secondary side. Now, since this panel is installed in a different building, it will also require a main. How do we do this without creating coordination issues?

The panel in the the other building does not require a main breaker, the building feeder requires a disco, 225.31, as long as the 1st disco can provide OCPD to satisfy 408.36 and protect the feeders also, 215.3.

The disco required by 225.31 has to be service rated, 225.36.
 

ASG

Senior Member
Location
Work in NYC
Occupation
Electrical Engineer, PE
May be I'm not understand what you're saying. It requires a disco so I thought the easiest/cheapest way to satisfy that would be with a main as opposed to finding space for an additional unfused disconnect switch.
 

jumper

Senior Member
May be I'm not understand what you're saying. It requires a disco so I thought the easiest/cheapest way to satisfy that would be with a main as opposed to finding space for an additional unfused disconnect switch.

The coordination issue you were referring to was the transformer disco vs the panel main correct?
 

iwire

Moderator
Staff member
Location
Massachusetts
May be I'm not understand what you're saying. It requires a disco so I thought the easiest/cheapest way to satisfy that would be with a main as opposed to finding space for an additional unfused disconnect switch.

Which will be cheaper, adding an unfused disconnect or getting and complying with coordination studies for a main breaker? I don't know the answer but I am sure that was what Jumper was suggesting. :)
 

jumper

Senior Member
Which will be cheaper, adding an unfused disconnect or getting and complying with coordination studies for a main breaker? I don't know the answer but I am sure that was what Jumper was suggesting. :)

It was exactly what I was suggesting.

It relieves the pressure of this part of OPs problem.

Yes, this is a hospital where we are feeding a new Emergency Mechanical Equipment panel.
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
Maybe I am missing something here.

My understanding is we have a separate building supplied by a feeder. The separate building needs a (service rated) disconnect at/near point it receives its supply.

Next item in the series is a transformer.

Unless there is two wire single phase or three wire three phase transformer output, in which most cases primary overcurrent protection can also protect the secondary, you will almost always need a main overcurrent device on the secondary.

Neutral conductor is not required if there is no load that utilizes a neutral. Equipment ground is required no matter what, unless allowed by previous code at time of installation to use the neutral for equipment grounding at a separate building.
 

iwire

Moderator
Staff member
Location
Massachusetts
Maybe I am missing something here.

My understanding is we have a separate building supplied by a feeder. The separate building needs a (service rated) disconnect at/near point it receives its supply.

Next item in the series is a transformer.

No, as I understand it the layout is more like this

First building > Service > Transformer > breaker > feeder to other building > panel in other building
 

ASG

Senior Member
Location
Work in NYC
Occupation
Electrical Engineer, PE
Yes, finding room for a non-fused disco might be difficult but a main breaker won't be coordinated with the fused disconnect.
 