Driven Ground rod material

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I found this taken from here

Comprehensive direct burial studies done by the National Bureau of Standards showed that 3.9 mils of galvanizing could be expected to provide 10-13 years of protection in most soils. This same study showed that 10 mils of copper could be expected to last more than 40 years in most soil types and is the basis for the 10 mils of copper required for a rod to be UL listed. Furthermore, independent ground rod testing performed by the Navy and the National Electrical Grounding Research Project back up the data gathered by the National Bureau of Standards. Because of these studies, a service life of 10 to 15 years can be assigned to galvanized rods and 40-plus years for 10 mil copper-bonded rods in most soil types.
 