Respectfully, I look at it differently. From the wording of 250.97, if the voltages are greater than 250v to ground, the box would have to be listed for grounding if you used concentric or eccentric knockouts. I find no mention of "clamps" and can see the where the question would arise, but find nothing so far that prohibits there use on 277v
I was specifically talking about metal boxes and clamps only. Not enclosures, cabinets or anything else.
From your earlier link:
All boxes with concentric or eccentric knockouts have been investigated for bonding and are suitable for bonding without any additional bonding means around concentric (or eccentric) knockouts where used in circuits above or below 250 V, and may be marked as such.
Clamps for armored cable, flexible metal conduit, metal-clad interlocking armor ground cable, metal-clad continuous smooth-sheath cable, or metal-clad continuous corrugated-sheath cable are considered suitable for grounding where installed in accordance with the NEC.