Does anyone have a link to documentation that discusses sizing of Medium Voltage Switchgear?
What do you mean by sizing? Physical dimensions?Does anyone have a link to documentation that discusses sizing of Medium Voltage Switchgear?
For example, let's say that I have a transformer, 10 MVA, 4160 V on the secondary side. I would like to size switchgear for this application.
For example, let's say that I have a transformer, 10 MVA, 4160 V on the secondary side. I would like to size switchgear for this application.
Well, you would size the switchgear for the loads, not for the transformer. But of course you have to take the limits of the transformer into consideration.
You might consider breaking up the service into smaller pieces. I.E, split gear up into four units and then locate one unit in each of the four corners of a large building for example. You certainly should also consult vendor for physical sizing per NEC 110. They take more clearance than typical switchboards.