I know there is a lot of discussion on wiring in a dialysis clinc. But what say ye on sconce lights that are 6 1/2' above the floor in the area where the dialysis chairs are located. I have an inspector who is questioning why we didn't wire them with healthcare cable.
Patient care area is defined in NEC 2008 517. It considers anything wired in a patient care area must comply with NEC 517.13. Basically you have to have a redundant grounding path. The only loop hole I see is possible a light above 7 1/2 feet which would put it outside a patient care vincinity. In which you do not have, you only have 6 1/2 feet.![]()
Also keep in mind that the exception in 517.13(B) for lights above 7-1/2' only allows you to omit the insulated equipment ground. You must still use a wiring method that itself is listed as being suitable as an EGC in accordance with 250.118.