cdcengineer
I have been posed a new one for me. The PV installer has designed an 8,280 W system to be beck-fed froma signle phase 208V inverter into a 208Y/120V distribution panel. The unbalanced interconnection (NEC 705.100) is not a concern, but the issue is with 705.12(D)(2).
We typically see residential and/or commercial systems where we tie in a breaker and add the sum of the back-feed breaker and the MOCP device. This resultant value cannot exceed 120% of the busbar or conductor. However, with a 45A/2P back-feed breaker and a 200A/3 MOCP, theoretically this is not acceptable due to 705.12 - allowed 1.2 x 200 = 240A versus proposed 200 + 45 = 245A.
I believe this article should read that the sum of the load (kW or kVA) rating of the circuitsd supplying a busbar or conductor shall not exceed that of the busbar.
The existing busbar is rated for 200A, 3-phase or 200 x 208 x SQRT 3 = ~ 72,053 VA x 1.2 (Per NEC 705.12(D)(2) ~ 86,464 VA, the 200A/3P main is rated for ~ 72,053 VA and the back-feed breaker is 45 x 208 ~ 9,360 VA. Thus 72,053 + 9,360 = 81,413 VA / 208 x SQRT 3 = 81,413 VA.
Anyone have any experience with something like this, or have an opinion on the interpretation of 705.12(D)(2)? Feedback, comments and input are greatly appreciated.