Underfloor Raceway and Conduit

Status
Not open for further replies.
I am working in an industrial environment and I am installing a small
control panel. There is an existing trough (underfloor raceway) cut
into the concrete that leads to the master control panel. All the
existing wires in the trough are run in conduit but I am wanting to
run a piece of SO cord alongside the conduit.

I would be running a SO cord for 120V power and a SO cord for
some control signals.

Is there any NEC restrictions on running SO cord inside the trough?
The cover of the trough is plenty stout. There is plenty of room in
the trough so fill percentage is not an issue.

Could multi-conductor tray cable be run in place of the SO cord
that has the control signals?

I have seen this done in other industrial environments by other
people.

Lucas
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
Not knowing what the controls are for, you may need to keep a certain distance from power, per manufacturer. i know this is an issue with distributed control systems.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
400.8(2)............what you are wanting to do is a Violation

(2) Where run through holes in walls, structural ceilings,
suspended ceilings, dropped ceilings, or floors

I don't see a problem here. Its not being run thru a hole.

A bigger problem IMO is 400.8(1).

is there some reason you can't run NM in the raceway? that would appear to be legal if you can legally run NM in your building.
 

Smart $

Esteemed Member
Location
Ohio
That is my opinion, despite it being a perfectly safe installation and something that is probably done in just about every factory everywhere in this country.
I do not disagree... but I will not advise anyone to do a non-compliant installation.

There are at least a few other cable types which are compliant.
 

kenaslan

Senior Member
Location
Billings MT
I would ask the AHJ. IMO the "trough" cut into the floor, is not the floor, so (2) would not apply. I would however also run it in conduit.
 