- Lockport, IL
- Semi-Retired Electrical Engineer
And he might have said so earlier, if he had not been out of town for the last week. :happyyes:I know Charlie wants us to look at it like you suggest. . . .
Once we get everything in the code clearly defined, we will have no need for this forum... I would like to see that clearly defined or explained within the NEC, but I doubt it will ever happen.
It might be interesting to compare NEC ampacities with other standards. I have no idea how they would compare. Is the NEC more conservative or less than other major wiring standards. :?
Certainly. In fact, 310.15(A)(2) exception may permit the use of 12 all the way - which is part of the turn I intend to take this. Not completely thought out yet though.
This is not exactly on point with George's original post, but I have question along the same lines. If you have a circuit that needs #10 due to roof top heat, but a #12 would otherwise be required, can you run the non roof portion in #12 and run the roof portion with #10 and be compliant?
Yes you can.
Although permitted by code it is IMHO poor practice and should only be considered if there is a substantial saving.
I feel that there is a risk that in the future that somone will observe the #10 and upsize the breaker to suit #10, not realising that part of the circuit is in #12.
Should be OK if the load center end is #12, but a bit dubious if the load center end is #10 and smaller wire is used out of sight of someone working on it in future.
Yes you can.