And he might have said so earlier, if he had not been out of town for the last week. :happyyes:I know Charlie wants us to look at it like you suggest. . . .
And he might have said so earlier, if he had not been out of town for the last week. :happyyes:I know Charlie wants us to look at it like you suggest. . . .
Once we get everything in the code clearly defined, we will have no need for this forum... I would like to see that clearly defined or explained within the NEC, but I doubt it will ever happen.
It might be interesting to compare NEC ampacities with other standards. I have no idea how they would compare. Is the NEC more conservative or less than other major wiring standards. :?
Certainly. In fact, 310.15(A)(2) exception may permit the use of 12 all the way - which is part of the turn I intend to take this. Not completely thought out yet though.
This is not exactly on point with George's original post, but I have question along the same lines. If you have a circuit that needs #10 due to roof top heat, but a #12 would otherwise be required, can you run the non roof portion in #12 and run the roof portion with #10 and be compliant?
Yes you can.
Although permitted by code it is IMHO poor practice and should only be considered if there is a substantial saving.
I feel that there is a risk that in the future that somone will observe the #10 and upsize the breaker to suit #10, not realising that part of the circuit is in #12.
Should be OK if the load center end is #12, but a bit dubious if the load center end is #10 and smaller wire is used out of sight of someone working on it in future.
Yes you can.
Although permitted by code it is IMHO poor practice and should only be considered if there is a substantial saving.
I feel that there is a risk that in the future that somone will observe the #10 and upsize the breaker to suit #10, not realising that part of the circuit is in #12.
Should be OK if the load center end is #12, but a bit dubious if the load center end is #10 and smaller wire is used out of sight of someone working on it in future.