If you are using a bonding bushing to bond a raceway for, say, a bad box connection in a system over 250 volts (reducing washers, oversize knockout, etc.), are you required to bond both ends of the raceway? I understand it is required for a raceway protecting a grounding electrode conductor.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
If you are using a bonding bushing to bond a raceway for, say, a bad box connection in a system over 250 volts (reducing washers, oversize knockout, etc.), are you required to bond both ends of the raceway? I understand it is required for a raceway protecting a grounding electrode conductor.

No, if it is otherwise connected at the other end by an approved method. Of course does not count if it is a service raceway, or as you said, a GEC.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
No, if it is otherwise connected at the other end by an approved method. Of course does not count if it is a service raceway, or as you said, a GEC.
The NEC does not require that service raceways be bonded at both ends, however some utilities do in their rules.
 