mallard duck
- Maryland
I have a project to install a 480 volt, 250/500 kW UPS between the transfer switch and the 600-amp MDP. The problem I found is the wiring from the 600-amp 100% rated GE breaker Spectra SGHA36AT0600 at the switchgear is feeding the ATS with 2 sets of 4/0. Between the 300 kW generator's 600-amp breaker is the same 2-sets of 4/0 and between the ATS and the MDP is the same.
Can someone tell me I am wrong to think all this wire and 2 inch conduit will need to be replaced with 300 KCM in 2-1/2" conduit.