north star
- inside Area 51
I have a Commercial application with a 40 ft. aluminum flag
pole being installed.........Nothing will be attached to the
flagpole itself, except a halyard [ i.e. - the rope ] for raising
and lowering the flag.
Will this flag pole be required to be grounded?........The
"below grade" foundation will not have any steel in it, but
will be filled with sand in to a cylindrical tube with a square
steel base.
NFPA 780, 2011 Edition, Section 4.2.2.3 says for aluminum
surfaces are not to come in to contact with copper, and
vice versa..........Section 5.4 addresses Metal Towers and
Tanks........Is a single flag pole considered a Tower?
In a preliminary search of this topic on the internet, I came
across something called a "PreVectron 4 Ease" thingy.
Allegedly, there are capacitors stored in something at the
top of the flag pole........When a storm is approaching,
...supposedly the capacitors are gathering energy from
the surrounding electrical fields, ...storing it and will release
this "stored energy" to create an "upward [ electrical ]
leader, that will connect with a naturally occurring lightning
"down leader", and then direct that charge; internally in
the flag pole, to the earth........See this link:
http://www.flagpole-installation.com/
Is this type of flag pole required to be grounded in some
manner?.......If so, what code sections [ from which code] are
applicable?
Thanks!
steel base.
applicable?
Thanks!