Service entrance conductors
kluchon
I have a 3phase service with the breaker in the meter socket. I ran 2/0 to a main lug panel. Commercial office building. Inspector says I can't reduce wire size from 3/0 in commercial. Not sure hel is correct? Can anyone help with code locations to support my side? I thought it was okay for under 400 amp. And wouldn't the wires be considered service lateral? Or even branch circuit?
the allowance in 310.15(B)(6) is for dwellings only, there is another thread that where Bob (iwire) explained where in 240 it doesn't allow 2/0 on a 200 amp service, and 230 where it also spell this out, I see if I can find the thread.
Here post 56
For a singe service disconnecting means 800 amp or less we can round up the next standard size breaker. That is as far oversized we can be. See 230.90(A) Exception 2 and 240.4(B)
3/0 is already sized for 200 amp so there is no rounding up as allowed in 240.4(B) as allowed in the exception #2 to 230.90(A) and 230.90 does not allow us to use calculated load unless we meet the exception #3 requirments, for using 500kcmil the yes we can use the rounding up to next breaker size for the 500's on a 400 amp service
...3/0 is already sized for 200 amp so there is no rounding up as allowed in 240.4(B)...
It's more that 2/0 is good for 175A with 75?C terminations, which is also a standard ocpd rating. There is nothing to round up. :blink:
If one could prove to AHJ, however unlikely, an ambient temp of 77?F or less, that would push the allowable ampacity of 2/0 to over 175A, which could then have an ocpd rounded up to 200A... provided the calculated load is less than the temperature-corrected ampacity of the 2/0.