altarengineering
Member
We recently designed an installation in which a 40 HP Submersable motor was served by a two pot transfomer bank... Each bank was 25 KVA resulting in a total of 50 KVA. Acknowledging that the 40 HP can be assumed equivalent to a 30 KW load (PF assumed to be unity) and the 50 KVA two pot bank derated to 86.6%, should the customer have any complaints. He is complaining about not having true three phase, and unless Im missing something, he's mistaken. He claims that had he know he was to be served from a two pot bank he would have set his equipment up differently, but now the current set up will cause him problems
Let me know your thoughts
Let me know your thoughts