Bill Annett
Senior Member
- Location
 - Wheeling, WV
 
- Occupation
 - Retired ( 2020 ) City Electrical inspector
 
Did an inspection today where the contractor ran NM cable from a panel on the first floor thru the second and third floor and then penetrated the roof with a short piece of  PVC conduit ,then to carflex, to a disconnect for an AC unit.  I told the contractor that NM could not be in a conduit outside because it is considered to be a wet location.  I am home and left my code book in the office but I think that I cited code section 300.9.  He said that if he strips off the jacket of the NM that he would be ok.  I do not agree with that.  His wiring method is NM.  It started out as NM and has no splices so I can not see how it now could not be NM.  AM I missing something? Any input will be appreciated.  Code references will even be better.
I did not have a good day at work. On the way home I stopped and bought some Chinese food. The fortune cookie said ? If you have a job without aggravations, you don?t have a job? The next time That I do not have a good day at work, I think that I will just get a Big Mac.
Thanks, I will check back to see your opinions. If I am wrong please let me know.
	
		
			
		
		
	
				