Transformer disconnect w/ double lugs sketch

Status
Not open for further replies.

Npstewart

Senior Member
Hi everyone. I ran into a electrician buddy of mine who is doing an install based on a sketch that an architect drew. He asked my opinion on it to see if it was legal. I re-drew the sketch real quick for purposes of this post. Over-all, this seems legal as long as the load doesen't exceed 200A, but this setup is extremely strange to me. I just wanted to get some opinions on it.


If you are wondering, I have no idea why they bought such a large transformer for such a small load and fused it down to 200A.
 

Attachments

  • SKETCH.pdf
    8.5 KB · Views: 1
Hi everyone. I ran into a electrician buddy of mine who is doing an install based on a sketch that an architect drew. He asked my opinion on it to see if it was legal. I re-drew the sketch real quick for purposes of this post. Over-all, this seems legal as long as the load doesen't exceed 200A, but this setup is extremely strange to me. I just wanted to get some opinions on it.


If you are wondering, I have no idea why they bought such a large transformer for such a small load and fused it down to 200A.

The 2 sets of 3/0 from the xformer seem useless, why not just use 1 set? You may have trouble getting lugs on the disconnect approved for this many conductors and have wire space issues as well. Why not 1 set of 3/0 to the 200 amp disco, then 1 set to the first panel (order it as a feed though), then to to the second panel with 3/0?
 
Maybe they got a deal on the transformer. I don't have a problem with it. If that is what they want to pay you to do, why would you care? I can't see any code violations. as someone mentioned you might have an issue with wiring room for the feeder into the disconnect.
 
I agree that there are probably 3 other ways to do this better. This is not my design though, I just duplicated the sketch that was given to me and was asked to give my opinion. If I were designing this, depending on the specifics, I would have installed a 75 KVA transformer and had one panel, if more spaces were required I would have sub-fed it or done a feed thru.
 
I agree that there are probably 3 other ways to do this better. This is not my design though, I just duplicated the sketch that was given to me and was asked to give my opinion. If I were designing this, depending on the specifics, I would have installed a 75 KVA transformer and had one panel, if more spaces were required I would have sub-fed it or done a feed thru.

Agreed. But I still say you can't put 16, 3/0 conductors in a 200 amp breaker enclosure or even in a safety switch.
 
Does seem a bit silly. For the cost of (1) additional 200 amp disconnect he could double his capacity. Everything else is already size to do so.
 
Does seem a bit silly. For the cost of (1) additional 200 amp disconnect he could double his capacity. Everything else is already size to do so.

It would probably cost less than whatever extra gutters it takes to make the wires fit in one disconnect.

I run across this kind of thing now and then. Often, it does not make much sense to me, but sometimes how it came to be almost makes sense when I know the whole story.

We have had customers specify PLC systems that cost tens of thousands of dollars to handle <20 I/O. We make sure that they udnerstand there are more cost effective options, but if that is what they want, that is what they get.
 