using 75 degree rating for conductor
tommyrice
I just had a disagreement with a friend of mine dealing with the allowable ampacity of a #14 thwn conductor to a 10 amp pool pump.I told him as long as the pump terminations were rated for 75 degrees and breaker was 75 degrees the phase wires could be #14 under a 20 amp breaker.He disagreed with me. I told him equip. grnding cond. had to be #12 but hot legs could be # 14 under these circumstances. Am I right?
I believe that 2011 NEC 240.4 (D)(3) has the answer to your question.
(D) Small Conductors. Unless specifically permitted in
240.4(E) or (G), the overcurrent protection shall not exceed
that required by (D)(1) through (D)(7) after any correction
factors for ambient temperature and number of conductors
have been applied.
(3) 14 AWG Copper. 15 amperes
have been applied.
240.4(D) does not apply in the example provided by the OP. 240.4(G) rules here. The #14 conductor in this case is correct, and the OCPD could be even larger than the 20 amp he used.
Sorry, my bad...
Recently took my exam so, of course, I think know everything! :ashamed1:
IMO you could use 14 awg with a #12 EGC on a 20 amp cir. As stated 240.4 (G) comes into play and if the termination are rated 75 C then #14 is fine at 20 amps.
Also remember that the OCPD can be rated 250% of the full load current. A 10 amp motor with 14 amp conductors and a #12 EGC could then be protected at 25 amps and avoid using a GFCI breaker.
We could also use a 14 AWG EGC as the EGC is never required to be larger than the circuit conductors.
I thought so also, but I do not know how to deal with this then:
680.21(A)(1)The branch circuits for pool-associated motors......
Any wiring method employed shall contain an
insulated copper equipment grounding conductor sized in
accordance with 250.122 but not smaller than 12 AWG.
OK, I did not know about that one, being in a later chapter it trumps 250.
I thought about that too, but 250.122(A) seems to be in direct conflict with 680.21(A)(1). What does the NEC Manual of Style say?
250.122 Size of Equipment Grounding Conductors.
(A) General. Copper, aluminum, or copper-clad aluminum
equipment grounding conductors of the wire type shall not
be smaller than shown in Table 250.122, but in no case
shall they be required to be larger than the circuit conductors
supplying the equipment
. Where a cable tray, a raceway,
or a cable armor or sheath is used as the equipment
grounding conductor, as provided in 250.118 and
250.134(A), it shall comply with 250.4(A)(5) or (B)(4).
680.21 Motors.
(A) Wiring Methods. The wiring to a pool motor shall
comply with (A)(1) unless modified for specific circumstances
by (A)(2), (A)(3), (A)(4), or (A)(5).
(1) General. The branch circuits for pool-associated motors
shall be installed in rigid metal conduit, intermediate
metal conduit, rigid polyvinyl chloride conduit, reinforced
thermosetting resin conduit, or Type MC cable listed for the
location. Other wiring methods and materials shall be permitted
in specific locations or applications as covered in
this section. Any wiring method employed shall contain an
I don't have the NEC handy but a section of Artcile 90 tells us that the later chapters modify or supplement the earlier chapters.
So 680 trumps 250. :D
90.3 Code Arrangement. This Code is divided into the
introduction and nine chapters, as shown in Figure 90.3.
Chapters 1, 2, 3, and 4 apply generally; Chapters 5, 6, and 7
apply to special occupancies, special equipment, or other special
conditions. These latter chapters supplement or modify the
general rules. Chapters 1 through 4 apply except as amended
by Chapters 5, 6, and 7 for the particular conditions
I have no doubt that 680 trumps 250. The only issue I would have is whether #14 would be allowed. I see no reason for it to be disqualified but 680 clearly states 12awg min. EGC. You could almost be assured that 12 awg circuit conductors would be used in most all cases.
Yeah, I would say this backs that up. As many times as I have read 250.4, you would have thought I would have seen this before.:slaphead:
250.3 Application of Other Articles. For other articles
applying to particular cases of installation of conductors
and equipment, grounding and bonding requirements are
identified in Table 250.3 that are in addition to, or modifications
of, those of this article.
It would make it less confusing if they just insisted on the circuit being run in a minimum of 12awg. I must say I have never seen an inground pool done with anything less than a 20 amp circuit.
I would also love to know why an inground pool of 20 amps or less must be gfci protected when we know they make gfci up to 50 amp.
Also there is no 3 phase gfci so no larger pools are gfci protected so why do we need it?? i have no issues using it but before 2005 we never wired the pumps with GFCI-- Why now since none of the other pools above 20 amp need it.