Ground Rod/conductor Size for Site Lighting

Status
Not open for further replies.

metallica5

Member
Location
Metro DC
Drawing detail for site lighting calls for 10' x 3/4" ground rods at concrete bases for parking lot lighting and bollard style walkway lighting for new retail building construction project. Detail also shows #8 bare copper bonding metal pole to ground rod. I assume engineer called for this to limit potential lightning damage. Crew installed 8' x 5/8" ground rods into poured bases by mistake. We do have equipment grounding conductors pulled in with circuit conductors. My question is: Will 8' ground rods with #8 copper be sufficient for intent or do we need to go back and install 10' x 3/4" with # 8 copper. I question the size of the #8 grounding conductor also. Thanks for feed back.
 
In my opinion, the concrete encased 8' rod is a much better ground than a single 10' rod. But my opnion doesn't count.

If the engineer/owner/inspector doesn't accept the installtion, try doing a ground resistance test comparing a single 10' rod and the foundation. Isolate the EGC so the test is reading just the one foundation/rod.
 
Yes, equipment grounding conductors were pulled in with circuit conductors separately. I questioned the #8 conductor as being underrated for capacity to the 10' rod but fine for the 8' rod?
 