Hi, I have a 400kw, wye generator, 480/277V, 3phase. All Loads fed from this generator are delta. Utility is 480V, 3phase delta. Currently neutral and ground are linked at the generator and only phase conductors are fed into a 3 pole transfer switch(no neutral cables). I was advised to remove the generator neutral ground link at the generator to increase system reliability and leave neutral floating. Idea behind this is to keep the generator main breaker from tripping in case of a ground fault. A ground fault monitor will be installed to find ground faults.
I would like to ask, does this sound like a good engineering approach, has anyone seen this? Which standards should I refer to get more information on this topic? Thank you.