I'm bidding an outdoor kitchen that will be completely detached from the house. It will be covered by a roof, but otherwise open on all sides. I've done outdoor kitchens before but they have always been on the back of the house. This completely detached kitchen will require approx. (6) 120v circuits, it seems like this set-up would be treated like a detached garage or shed requiring a separate sub-panel and ground electrode since more than (1) 120v 20a circuit will be run to it. Anyone come across this before?
Thanks
Ponchik
CA
Electronologist
I agree. Install a subpanel and pound in two grounds rods.
But if it is being built and assuming the slab or foundation is new then can't the OP use the rebar & water pipe instead of the two ground rods?
stickboy1375
Litchfield, CT
You could use a CEE, then you wouldn't need the ground rods... if the water pipe meets the criteria of 250.52 (A)(1) it needs to be part of the grounding electrode system regardless.
jumper
Foundation or footing- yes, slab-no.
250.52(A)(3) Concrete-Encased Electrode. An electrode encased
by at least 50 mm (2 in.) of concrete, located horizontally
near the bottom or vertically, and within that portion of a
concrete foundation or footing that is in direct contact with
the earth,
stickboy1375
Litchfield, CT
the earth,
I was trying to justify a slab myself, just wasn't sure if a slab met the definition of a foundation. Seems to me that it does?
Foundation: the lowest and supporting layer of a structure
hillbilly1
North Georgia mountains
Owner/electrical contractor
Since it has a roof, it may have footers unless they bury the posts holding up the roof. If they have a fireplace or wood fired pizza oven, they will also have footers.
titan1021
The kitchen will sit on top of a large patio, the roof structure will be supported by four large columns. It will have a brick pizza oven and two barbeques, along with a dishwasher, disposal, and refrigerator.
infinity
New Jersey
Journeyman Electrician
Even if they put in footings for the columns they would need 20' or more of 1/2" or larger rebar to qualify as a CEE. IMO it's not very likely that these footings would contain that rebar so two rods might be all that's required.
Ponchik
CA
Electronologist
are you sure this is a kitchen and not a restaurant. :D It must be a huge house.
Ponchik
CA
Electronologist
I am trying to guess where.
Marin, Napa, or Sonoma are my first 3 guesses.
Besides the above Palo alto, los altos hills, wood side, atherton have some huge homes. I don't do much work in these homes except troubleshooting and service work but every time i am in these homes, i get lost in the house.
jumper
Yeah, nice areas also. OP has his location as North CA, so I tend to think of I-80 and above. Just an old habit from way back.
titan1021
Great guesses! Those are great places to work, people have money and aren't afraid to spend it on on their projects.
They usually want the latest and greatest installed.
So many times I see GC's or clients want to cut corners on electrical when doing a project, its a shame to see a nice project totally miss the boat on lighting design.
This project is in Vacaville. Their will also be recessed lights, ceiling fan, flat screen, ceiling mounted propane heaters, etc...