texie
Senior Member
- Location
- Fort Collins, Colorado
- Occupation
- Electrician, Contractor, Inspector
I have a situation with a customer that has had issues with loss of 1 phase on primary side of the 500 KVA POCO owned transformer that serves only them. This has happened 4 times in 3 years due to storms. The service is 208/120Y, 4000 amp protected by a SQD Powerpact breaker. I'm wondering about the wisdom of adding a phase loss kit to the breaker to open it on phase loss. Or would it be better to add shunt trip and use a stand alone phase loss detector. Does anyone have have any opinions about the reliability of phase loss detectors on the secondary of a transformer to detect a phase loss on the primary side?