NEC 220.55 - Multi-Family Calculation with Different SIze Rage & Cooktop

Status
Not open for further replies.

cdcengineer

Senior Member
Alright, good-morning all.

I am posed with a new one here this morning. I have (28) dwelling units, (14) with 8kw range & (14) with 2.766kW cooktops. The units are served with 120/208V, 1-phase, but the distribution panel which serves this bank of units is 208Y/120V, 3-phase.

220.55 allows where two or more single phase ranges are supplied by a 3-phase feeder, the total load shall be calculated on the basis of twice the number connected between any two phases.

Therefore we have a max of (5) ranges and (5) cooktops connected between any two phases. I was originally under the impression that I should calculate the ranges as:

Twice the maximum - 2 x 5 = 10, table 220.55 --- Column C - 25kW+(25kW/2) = 37,500

And the cooktops should be handled as:

Twice the maximum - 2 x 5 = 10, table 220.55 --- Column A 49% x (10 x 2.766kW) = 13553 + (13553/2) = 20,330

Total Electric Cooking = 37,500 + 20,330 = 57,830

However after reading a bit closer, I'm now considering that table 220.55, note #3 applies. Which after still considering that there are only (5) of each type of cooking appliance connected between any two phases, this would result in the following:

Cooktops - Twice the maximum - 2 x 5 = 10, table 220.55 --- Column A 49% x (10 x 2.766kW) = 13553 + (13553/2) = 20,330

Ranges - Twice the maximum - 2 x 5 = 10, table 220.55 --- Column B 34% x (10 x 8kW) = 27200 + (27200/2) = 40,800

Total Electric Cooking = 20,330 + 40,800 = 61,130

And finally there is always the possibility that this should be handled as if all the appliances are combined:

Twice the maximum - 2 x 10 = 20, table 220.55 --- Columns A & B [35% x (10 x 2.766kW)] + [28% x (10 x 8kW)] = 32081 + (32081/2) = 48,122

I have performed multi-unit calculations before, but never with different size electric cooking appliances. Can anyone provide some opinions on how this should be handled?

As always, your input is greatly appreciated.
 

cdcengineer

Senior Member
Alright, after further deliberating, it is my interpretation of 220.55 that the following is how to handle this situation:

Twice the maximum # of appliances connected between any two phases - 2 x 10 = 20, table 220.55 --- Column C = 35kW, divide by 2 and multiply the result by 3, this will give us the equivalent 3-phase load = 52,500

This is also after considering Annex example D5a which shows that if these appliances were of the same load rating at 8kW, than this would result in a lower total electric cooking appliance load than I had calculated in my first attempt indicated above.

Quiet here today. Might be a good sign everyone is busy at work.
 

mcnut

Member
Location
Florida
heard a pin drop...

heard a pin drop...

Do the 14 units with the cook tops have additional cooking appliances like single or double ovens?
When there is a cooktop here in Florida it is usually paired with a another appliance.
 

drateenergy

New member
Location
Buffalo, NY
250.55

250.55

28 Units
14- 8kw Ranges
14- 2.766 Cooktops

Everything should be done separately right to the end. as you said they are in different unit types

maximum # connected between any two phase = 5 C Phase and A phase darw it out if u have to.
2 x 5=10
8000 x 10 = 80000va
column B 10 = 34%
80000 x .34 = 27200va
single phase 27200/2 = per phase 13600va
three phase 13600 x 3 = 4533 va

so on and so forth do the same with the cooktops and total up your 3 phase service Va.
hope this helps.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
"Multi-Family Calculation with Different SIze Rage & Cooktop"

I would imagine multiple families living together with only one range would cause them to have different levels of rage..............:lol::lol::lol::lol::lol:

Couldn't resist!:D
 