travish
 - Central North Carolina
 - Electrician
I am using a 150kva delta/delta 480 to 240 xformer in reverse. so I am feeding 240 to the xformer and getting 480 delta out of the other side. My trouble is the Primary side (which is my secondary side) has no neutral tap. Because it is designed to be the primary. So that leaves me 3 options, Should I ground 1 corner? Buy a ground detector and leave the ground floating? Buy the right xformer? The machine has a 100hp VFD and a 25hp VFD. The machine is only staying at our plant until December we would then ship the machine out to the midwest to one of our manufacturing plants (they have 480 availible). I used the xformer because we had it. We have been runing the machine for about 2 months. Now after thinking about the situation I am scared for safety reasons. If I ground 1 phase and I have a ground fault we get 480 to ground and can the drives deal with the grounded phase? If I don't ground is there any down side (mainly safety)? A new xformer is about $3500
What do you think is the best option
Travis
Travis