geoff mickelson
I have a question as reguards a grounding source for a1600a 120-208 service. We installed a 10' grounding ring by the utility transformer along with the grond rods in the secondary side of the transformer and brought a bare 4-0 into the MDP. The inspector tells by code we also have to have a 3-0 attached to to the water pipe attached within 5' of the water pipe where it enters the building. We complied. My question is as I read the code tome it says you can use one of serveral methods not that you shall use use a water pipe if you comply with the other alternatives. What say you? Thank-you Geoff Mickelson R&G Electric Humboldt,Ia