Conduit protection?

Status
Not open for further replies.

RESI

Member
Location
Virginia
Just recently installed an air cooled generator and had it inspected. The 3/4" conduit from the residence to the generator goes underground. I used schedule 80 conduit at each end where it comes out of the ground. The Inspector said I needed to protect the conduit riser at the generator end from lawnmower/trimmer damage. I thought that installing schedule 80 conduit was the protection. I plan on calling the Inspector to talk about it but just wanted other's opinions. If you had to protect the conduit, what would you do? I thought about sliding a section of 1 1/2" conduit over the existing conduit and let it stick out above ground about 8 inches. Thanks to all who reply.:?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree with both of you.

Here is what I found on a pvc manufacturers site. The regular PVC is just called Heavy Wall.

Bullet.gif
PVC Rigid Nonmetallic Conduit (Extra Heavy Wall EPC-80)
Bullet.gif
Listed for use in aboveground and belowground applications including areas subject to physical damage.
Bullet.gif
Rated for use with 90?C conductors
Bullet.gif
Superior weathering characteristics
Bullet.gif
Identified for use in areas subject to physical damage in accordance to 352.12(C)
Bullet.gif
494* Series
Bullet.gif
1/2” – 6 ” Standard Radius and Special Radius Elbows available.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Maybe the inspector considers that area to be subject to severe physical damage.

Not that this dictates fact, but Schedule 80 PVC is used throughout the country down a power pole to feed utility transformers underground. The generally carries 12KV cabling. And your inspector wants to deem a generator feed inadequately protected?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Just recently installed an air cooled generator and had it inspected. The 3/4" conduit from the residence to the generator goes underground. I used schedule 80 conduit at each end where it comes out of the ground. The Inspector said I needed to protect the conduit riser at the generator end from lawnmower/trimmer damage. I thought that installing schedule 80 conduit was the protection. I plan on calling the Inspector to talk about it but just wanted other's opinions. If you had to protect the conduit, what would you do? I thought about sliding a section of 1 1/2" conduit over the existing conduit and let it stick out above ground about 8 inches. Thanks to all who reply.:?

I am inclined to agree that over time weed whacker damage will become apparent. Whether the code requires additional protection is something else. Some kind of sleeve is probably easiest, and will cost less than fighting over it.
 

renosteinke

Senior Member
Location
NE Arkansas
I'm inclined to say "humor the inspector."

Ultimately, it's a judgement call whether an installation is adequately protected. For example, I've seen a lovely EMT installation completely trashed by repeated impacts from pallet jack / stock picker / forklift traffic. In that instance, IMO, it would have been reasonable for the AHJ to require the conduit to be moved, or better protected.

Your inspector has looked at your instal, and has forseen a particular, very predictable hazard from ordinary maintenance.

Since the pipe is already in place, it's probably easiest to 'sleeve' the most exposed sides with a bit of strut.
 

kwired

Electron manager
Location
NE Nebraska
I'm sorry but this is worth a fight with said inspector. He needs to know he is not God.

What is the chance that same installation has the main service lateral just a few feet away in a Schedule 80 PVC and he has nothing to say about that?

Even RMC can be physically damaged although it takes more abuse to get it done.

One needs to know what abuse is likely when determining what physical protection is needed - but you never really know what will really happen. What if this install is facing the street and an out of control motorist hits it? There is something likely to damage it if it happens, but is not necessarily that likely to happen, not to mention there is likely damage to more than just this raceway if that happens.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
One needs to know what abuse is likely when determining what physical protection is needed - but you never really know what will really happen. What if this install is facing the street and an out of control motorist hits it? There is something likely to damage it if it happens, but is not necessarily that likely to happen, not to mention there is likely damage to more than just this raceway if that happens.

If there is grass planted where the PVC pipe comes up thru the ground, it will almost certainly sustain damage from both lawn mowing and weed whacking. It is not just likely, it is all but certain.

The question is whether the damage that will be incurred merits additional protection.

I am never a fan of giving in to the bureaucrats when they are just being power mad control freaks :) but this seems to me to be a legitimate concern.
 

kwired

Electron manager
Location
NE Nebraska
If there is grass planted where the PVC pipe comes up thru the ground, it will almost certainly sustain damage from both lawn mowing and weed whacking. It is not just likely, it is all but certain.

The question is whether the damage that will be incurred merits additional protection.

I am never a fan of giving in to the bureaucrats when they are just being power mad control freaks :) but this seems to me to be a legitimate concern.

There are millions of schedule 80 risers out of the ground subject to lawn mowers and weed whackers. I'm willing to bet only a very small percentage are ever damaged and it is likely that somewhat unusual situations have occured when they are damaged.

Brush blade on the trimmer instead of using typical nylon line would cause damage. It would also cause some damage on RMC although one incident like that would likely just result in a scratch.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
There are millions of schedule 80 risers out of the ground subject to lawn mowers and weed whackers. I'm willing to bet only a very small percentage are ever damaged and it is likely that somewhat unusual situations have occured when they are damaged.

Brush blade on the trimmer instead of using typical nylon line would cause damage. It would also cause some damage on RMC although one incident like that would likely just result in a scratch.

I would bet it is closer to all of them get damaged. The question would be whether the level of damage makes additional protection necessary. Even just a nylon string trimmers will damage PVC. Whether it does more than just mark it up or not is another discussion.
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
Does the inspector know you used sch 80, or did he just see PVC and not look at the markings? Wondering if he thought it was sch 40.
 

kwired

Electron manager
Location
NE Nebraska
Even just a nylon string trimmers will damage PVC.

I'm sure it can. Just how long do you suppose it takes to damage enough to compromise the integrity of the raceway.


If you sleeve the raceway with a larger piece of PVC you only get twice the lifetime of physical protection because it will damage the sleeve then racway and now it needs repaired. Guess we need to use RMC or encase it in concrete, or better yet encase RMC in concrete, wait, concrete is subject to damage by jackhammers:lol:
 

kwired

Electron manager
Location
NE Nebraska
How to fix damaged PVC.

I posted this last year.

http://forums.mikeholt.com/showthread.php?t=136356

Did not read that whole thread but the best way to protect that from a snow plow would be with some bollards. Even RMC may be damaged by the snow plow. Worse than damaging the raceway is if the plow would happen to pull on a conductor and destroy the equipment the conductor was connected to.

Had a helper a few years ago. We just finished pulling some underground supply conductors to a panel at a site for grain storage bins. His next task was to trench another line that happened to come close to the line we just pulled. He knew it was there, and that he was to run the trencher shallow and hand dig the rest of way to existing line yet he managed to hit the line. Not only did it break the raceway it pulled a conductor which pulled on the main breaker, broke the main and tried to pull part of the main through the raceway. My patience was not very good that day, I ended up just telling him he had to fix it and tried to stay away from him as much as possible until it was done, which was probably a smart thing.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
I would bet it is closer to all of them get damaged. The question would be whether the level of damage makes additional protection necessary. Even just a nylon string trimmers will damage PVC. Whether it does more than just mark it up or not is another discussion.

As I stated earlier, schedule 80 riser is a typical installation for 12KV transformer primaries. Should we go through the Country changing all of them out?
 

elohr46

Senior Member
Location
square one
I've been weedwacking against my underground PVC service conduit for 37 years now, still not damaged. Ruined about 8 weedwackers though.
 

renosteinke

Senior Member
Location
NE Arkansas
I think the question we're really asking is: Who gets to decide what protection is needed?

One approach is to assign the duty to some outside, uninvolved, expert, and let him make the call. That's what the inspector is doing. That's what many folks assert is right and proper every time we have a new code cycle.

Another approach, the more traditionally "American" approach, is to let the FREE citizen decide - and rely upon the market to help him.

"Lawn mower damage" is a very good example to use to illustrate this point. I've some rather flimsy solar lights simply stuck in the ground along my walkway .... and I've managed to not damage them at all in the past year.

By way of contrast, the nearby apartment complex has steel light poles that are leaning, or bent, or otherwise show damage, all from the activities of the grounds crew. It is almost as if these guys make it their mission to break things.

The usual response in that second situation is to keep patching things - until they get tired of 'minimal' stuff being broken, and take it upon themselves to beef things up.

There are just too many variables, too many judgement calls, for this situation to have a single answer. The OP needs to consider that the inspector just might have a better grasp of reality than he does .... and the inspector needs to know the difference between 'good design' and 'good law.'
 