Is it a violation to notch out a opening in a 2" weather head pipe and run SER through it and along the outside of the house to relocate the meter and sevices panel? I have a picture but I don't know how to download it.

Thanks, Gus
 

pete m.

Senior Member
Location
Ohio
Not really sure what you mean by "notching" an opening in the pipe... but the SE cable routed on the exterior is not a violation as long as it isn't subject to physical damage.