Grounded conductor sizing

Status
Not open for further replies.
Art. 250.24 C2 Can someone make it clear if this article is sizing the grounded conductor off the total circular mil area of all ungrounded phase conductors in the parrallel set? or off of the total cm of one set. (assuming that they are talking about total circular mils of a single phase conductor, and not the cm total of all three phases.)
Everybody seems to have a different interpretation.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The grounded conductor size is based on the size of the largest phase conductor in that raceway. If you have more than one conductor per phase in the raceway, then it is based on the sum of the conductors that make up the largest phase.
 
That is what my interpretation was, but I have an inspector looking for a larger grounded conductor, The application is 3 parallel 350 kcmil tray cables in parallel. The way I read this article I need to have a 1/0 grounded conductor per cable. With either a #2 awg Supply side bonding jumper per cable, or a single 2/0 supply side bonding jumper from my 1st disconnecting means, back to the transformer frame.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Are these service conductors or feeders? Are we talking about the neutral (grounded) conductor or an equipment grounding conductor or a supply side bonding jumper?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
That is what my interpretation was, but I have an inspector looking for a larger grounded conductor, The application is 3 parallel 350 kcmil tray cables in parallel. The way I read this article I need to have a 1/0 grounded conductor per cable. With either a #2 awg Supply side bonding jumper per cable, or a single 2/0 supply side bonding jumper from my 1st disconnecting means, back to the transformer frame.

250.24(C)(2) would require a conductor from Table 250.66 based on 350 X 3 = 1050 KCM. That would be a 2/0. I'm afraid the inspector is right (I'm assuming this is all copper).
 
Also, there is no neutral load. Just trying to make sure I am understanding the article correctly, the change to the 2011 code was "in the raceway" It does not mention cables. My interpretation is that a tray cable is it's own raceway. But it does not say raceway, or cable. and it does not say raceway/s. Which would change the meaning entirely. Any thoughts?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Is there an "XO" terminal on the transformer secondary? If so, is it used and is it bonded to a grounding electrode system?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Also, there is no neutral load. Just trying to make sure I am understanding the article correctly, the change to the 2011 code was "in the raceway" It does not mention cables. My interpretation is that a tray cable is it's own raceway. But it does not say raceway, or cable. and it does not say raceway/s. Which would change the meaning entirely. Any thoughts?
I don't think 250.24 even applies to this installation, however the wording in 250.30(A)(3)(b) is much the same.
 
Back to the origional question new article

Back to the origional question new article

The grounded conductor installed in parallel, for the grounded conductor in each raceway, is it to be sized for "the total circular mil area of the parallel dervied ungrounded conductors in the raceway"? (singular) or all the raceways in the parallel set? And is a tray cable, in the intention of this article to be considered like a raceway?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The grounded conductor installed in parallel, for the grounded conductor in each raceway, is it to be sized for "the total circular mil area of the parallel dervied ungrounded conductors in the raceway"? (singular) or all the raceways in the parallel set? And is a tray cable, in the intention of this article to be considered like a raceway?
Although a tray cable is not a raceway by definition I would think that that is the intent of the article
 