Grounding Requirements for seperate structure

Status
Not open for further replies.

KWH

Senior Member
I am going to feed a seperate structure from a panel 120/240 single phase and understand you need a fourth wire for the ground, concerning the ground rod at the new structure do you need one ground rod or two. ( there is no ufer, plumbing or steel )
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I am going to feed a seperate structure from a panel 120/240 single phase and understand you need a fourth wire for the ground, concerning the ground rod at the new structure do you need one ground rod or two. ( there is no ufer, plumbing or steel )

2 ground rods and don't bond the neutral at the out building disconnect.
 

kwired

Electron manager
Location
NE Nebraska
If you can prove the first rod has a resistance of 25 ohms or less you don't need the second one. Most people don't want to spend the $$ to have equipment that tests this or take the time to do it via alternate methods and therefore drive second rod and don't worry about what the resistance is. This is in 250.53(A)(2) - the exception afterward is where the 25 ohm or less portion is mentioned.
 