Our power voltage is 208v. The new equipment requires 240v +/- 10%. We have 204v at the outlet. The company has instaled a buck-bost trans. out of the panel and then back throug the panel to feed the outlet the now 240v. Is alowed ??? Artical number please. THANKS
More information please....
1. Who is the "company", the manufacturer of the equipment or the electrician doing the installation?
2. Is the "panel" the loadcenter or a panel associated with the equipment?
You have peaked my curiosity why either of these question would impact the answer.![]()
Our power voltage is 208v. The new equipment requires 240v +/- 10%. We have 204v at the outlet. The company has instaled a buck-bost trans. out of the panel and then back throug the panel to feed the outlet the now 240v. Is alowed ??? Artical number please. THANKS
It is allowed.
As far as an Article number I can't give you one that allows it but more importantly there is no Article prohibits it.
What are you specifically concerned with?
You have peaked my curiosity why either of these question would impact the answer.![]()
Take a look at 312.8 and if you are not looking at the 2011 code, make sure that you read the complete section.I am concerned about it going back through the panel then to the recptical. This is not an OEM item this was installed after the equipment by a contractor.
I am concerned about it going back through the panel then to the recptical. This is not an OEM item this was installed after the equipment by a contractor.