fst442
- Vancouver, WA, USA
My apprentice and I are having a debate. We have a 240V, 3 ph, center tapped delta(high leg) system in an industrial setting. A 200A fused disconnect supplies the existing 200A, 3ph panelboard. This panelboard supplies a 100A, 1 ph panelboard that is located right next to it and supplies 120V lighting loads. The panels are aging and need to be replaced to ensure selective coordination, proper AIC ratings, etc. The high leg makes the 1phase panel kind of necessary to keep the installation clean in my opinion. We are now gearing up to replace the panels and this question has come to mind. Any help would be greatly appreciated. Thanks.
1: Is it acceptable to feed the new 1 ph panelboard with 2 of the 3 feed thru lugs on the bottom of the new 3ph panelboard? Assuming, obviously, that we size the feeders so that they are protected and the second panel is of the same voltage rating as the first panel. I've never done it this way. My apprentice believes this would be an acceptable installation, however, I worry that this would be a poor installion.