Looking at job with existing service, there is going to be a building addition
Existing service is 480 volt 3phase 4 wire 1200amp rated no main with 5 spaces in use with one spare
Fed by 2 runs of 2" pvc with (4) 3/0cu wires per conduit
These wires terminate in a above ground cabinet (splice box ) The POCO transformer feeds this box.
The building owner wants the exact same setup for addition fed thru (2) 2" spare conduits coming from same junction box.
Would this be considered one service since there is only one set of secondarys coming from xfmr and if this falls under one service I will need a main breaker on the addition to stay under the 6 handle rule also the spare in the existing gear wouldnt count against you would it.
I also know they would be limited to a 400amp main based on the 2" conduits.