cdcengineer
I've been reading old posts on teh forum for the last hour.  I did not see any specific discussion regarding calculations for wye-delta high elg systems.
I have a project (only 2nd time I've seen this) where the building has a 2nd service fed from two 25kW 1-phase xfmr's. The system is 120/240V wye-delta (closed) with the high leg on B phase reading roughly 219V to neutral or ground.
My question: Would we calculate the total current on the system with a 3-phase 30kVA load as:
#1 - 30000/240(SQRT(3)) = ~72A
Or #2 30000/208*(SQRT(3)) = ~83A
I believe it is option #1 above, but I see some say it is #2. Another thing to consider, if we add single phase loads into the mix (served only from A & C phases), how does that impact the calculation?
Any feedback is greatly appreciate.