Received a call from an electrical contractor today, they have been struggling with this issue for a week.
They have a chiller that is going out on current imbalance, at 50% load a 50% current imbalance from the average currents will shut the chiller down. Above 50% load the chiller shuts down at 30% from the average (this is the average of all three phases. The percentages seemed high to be. They have been going down several times a day. Finally they installed a generator to handle just the chiller.
This is a WYE, DELTA starter.
What we did
Measured all phases
VAC
A-215, B-210, C-216
IAC
A-49, B- 69, C-74
We then rolled the phases and the current followed the conductor.
The chiller remained on line with this phase imbalance.
They has previously (prior top me arriving on site) connected the chiller to generator, they had been running off generator for several days. But restored the operation to utility today
While on generator this was what they recorded
VAC
A-209, B-209, C-209
IAC
A-75, B-75, C-75
These are the largest motors on site but I checked other smaller 3 phase motors and there was phase imbalance but the percentages were not nearly so severe. Additionally as the chiller loaded up the current imbalance was not as significant as at the lower loads.
I know phase voltage imbalance will result in current imbalance but the voltage phase imbalance is about 3% (varies during the day, I am told) and for the voltage imbalance the current imbalance we see seems excessive.
The day this started the utility had an issue on the network feeding this facility, they have not said what the issue was. The site was down about 13 hours before power was restored. This issue started after the power was restored.
The mechanical contractor says all systems on the chiller checked out OK.
We are in the process of monitoring the service and feeder for the chillers, and the utility is starting an investigation as well.
Any help would be appreciated.
They have a chiller that is going out on current imbalance, at 50% load a 50% current imbalance from the average currents will shut the chiller down. Above 50% load the chiller shuts down at 30% from the average (this is the average of all three phases. The percentages seemed high to be. They have been going down several times a day. Finally they installed a generator to handle just the chiller.
This is a WYE, DELTA starter.
What we did
Measured all phases
VAC
A-215, B-210, C-216
IAC
A-49, B- 69, C-74
We then rolled the phases and the current followed the conductor.
The chiller remained on line with this phase imbalance.
They has previously (prior top me arriving on site) connected the chiller to generator, they had been running off generator for several days. But restored the operation to utility today
While on generator this was what they recorded
VAC
A-209, B-209, C-209
IAC
A-75, B-75, C-75
These are the largest motors on site but I checked other smaller 3 phase motors and there was phase imbalance but the percentages were not nearly so severe. Additionally as the chiller loaded up the current imbalance was not as significant as at the lower loads.
I know phase voltage imbalance will result in current imbalance but the voltage phase imbalance is about 3% (varies during the day, I am told) and for the voltage imbalance the current imbalance we see seems excessive.
The day this started the utility had an issue on the network feeding this facility, they have not said what the issue was. The site was down about 13 hours before power was restored. This issue started after the power was restored.
The mechanical contractor says all systems on the chiller checked out OK.
We are in the process of monitoring the service and feeder for the chillers, and the utility is starting an investigation as well.
Any help would be appreciated.