Hello all - I have the following loads (VA) entered into our spreadsheet for a 208v, 1 phase service/feeder calc for an EXISTING dwelling unit (apartment) where the FPE loadcenters are being replaced:
1,476 (492 sq. ft at 3 VA/sq. ft)
1,500 (small appl. B/c - only 1 existing)
8,000 (electric range)
131 (hood fan/light)
4,000 (electric water heater)
6,375 (electric heat, baseboard)
(No laundry, bath EF, disposal, D/W, etc.)
20,842 (total after gen ltg & small appl., and 'other loads' at 75% demands taken)
divided by 208V 1 phase = 100 amperes.
Question is - what should the main breaker in the apartment loadcenter be? 100A? Or do some/any of these loads have to be considered continuous? And if so, do I have to add 25% of those loads per 215.3??? (i.e. is the loadcenter buss a 'feeder' per definitions?)
(Existing main CB is 125 amps - but Eaton cannot supply a UL listed retrofit kit for this box with a 125A main - they need the main to be 100A or less to fit in this existing, tiny FPE box. I assume due to wire bending space.)
Thanks.
1,476 (492 sq. ft at 3 VA/sq. ft)
1,500 (small appl. B/c - only 1 existing)
8,000 (electric range)
131 (hood fan/light)
4,000 (electric water heater)
6,375 (electric heat, baseboard)
(No laundry, bath EF, disposal, D/W, etc.)
20,842 (total after gen ltg & small appl., and 'other loads' at 75% demands taken)
divided by 208V 1 phase = 100 amperes.
Question is - what should the main breaker in the apartment loadcenter be? 100A? Or do some/any of these loads have to be considered continuous? And if so, do I have to add 25% of those loads per 215.3??? (i.e. is the loadcenter buss a 'feeder' per definitions?)
(Existing main CB is 125 amps - but Eaton cannot supply a UL listed retrofit kit for this box with a 125A main - they need the main to be 100A or less to fit in this existing, tiny FPE box. I assume due to wire bending space.)