got hit with a violation from a trough to a panel nipple was 26"
as per chapter 9 table 1 #4 max nipple 24" cant find any other reference to max size of nipple.
any thoughts
so at 26" it becomes a short conduit run and all the provisions of conduit fill and derating come into effect.
and of course since its more then 18" it must be supported.