I saw this in a Q&A in a magazine. They are supposedly answered by "code experts".
Do you agree with the answer given here?
Question
Are receptacle outlets installed above overhead kitchen cabinets permitted by National Electrical Code? If so, are the receptacles required to be on a small-appliance branch circuit that serves only audio-visual (A/V) equipment 9 feet above the floor?
Answer
The NEC does not specify a minimum or maximum mounting height for general-purpose branch circuits receptacles on a wall. Section 210.52(B)(3) requires additional small-appliance branch circuits to supply receptacle outlets in the kitchen and other rooms specified in 210.52(B)(1). Two or more 20- ampere small-appliance branch circuits required by 210.11(C)(1) are required to serve all wall and floor receptacles covered in every kitchen., per 210.52(B)(1).
Do you agree with the answer given here?
Are receptacle outlets installed above overhead kitchen cabinets permitted by National Electrical Code? If so, are the receptacles required to be on a small-appliance branch circuit that serves only audio-visual (A/V) equipment 9 feet above the floor?
Answer
The NEC does not specify a minimum or maximum mounting height for general-purpose branch circuits receptacles on a wall. Section 210.52(B)(3) requires additional small-appliance branch circuits to supply receptacle outlets in the kitchen and other rooms specified in 210.52(B)(1). Two or more 20- ampere small-appliance branch circuits required by 210.11(C)(1) are required to serve all wall and floor receptacles covered in every kitchen., per 210.52(B)(1).