Directional Protection on a Motor
MD88
Hi guys, I've noticed that on Multilin M60 and other high end motor protection relays, directional overcurrent for phase and ground is available... the only scenario I can see wanting this is if there's a fault on another feeder off the same bus and the motor starts feeding it, you would block tripping on the motor feeder breaker until the faulted feeder is cleared...?
Thanks
Thanks
Since 3ph motors rely on a given phase sequence that determines the direction that they rotate there would be devastating consequences should one of the phases as provided from the POCO be reversed.