Load Switching double throw disc.

Status
Not open for further replies.

Npstewart

Senior Member
I wasn't sure what to title this thread.

Lets say you have two loads, a table saw and a ban saw coming from two different circuits, both 208-1. Lets also say you want to devise a way so that these loads never run simultaneously. Is there a good way to do this without using a bunch of relays and contactors?

Do you think it would be possible/permissible to use a non-fused double throw disconnect assuming the over current protection for each circuit is sized properly and the disconnect ampacity rating is greater than the load, then size the branch circuit wiring for the larger load.

This has nothing to do with load calculations or service sizing.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
120612-1324 EDT

A DPDT switch of adequate voltage and current rating and switching only one wire to each motor will logically accomplish the goal. Also you can do this with a contactor with isolated contacts, one NO, and the other NC. Add two more isolated contacts and you can switch both lines to each motor. Just draw out the circuits to see how it works.

,
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I cannot think of anything more complicated than doing this 'your way' with switches.

You can buy a single 4-pole contactor with 2 'open' contacts and 2 'closed contacts.
Coil off = load 1, Coil on = load 2. Use a 208V coil and you can get the power from one of the circuits.

Or
You use two 2-pole contactors and a small double throw switch to control them.
 

Npstewart

Senior Member
Why would you say the double throw was complicated? Just asking so I know.

I would think the double throw method would be simpler but more expensive.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Why would you say the double throw was complicated? Just asking so I know.

I would think the double throw method would be simpler but more expensive.

Unless I'm missing something here, your way seems pretty simple and straight forward to me and maybe just as inexpensive in this size range.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Why would you say the double throw was complicated? Just asking so I know.

I would think the double throw method would be simpler but more expensive.

You said you had two different circuits supplying two different loads. I interpret this to be 4 incoming wires and 4 outgoing wires. A double throw switch is 4 incoming wires and only 2 outgoing wires.

How many amps are you looking at switching?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
You said you had two different circuits supplying two different loads. I interpret this to be 4 incoming wires and 4 outgoing wires. A double throw switch is 4 incoming wires and only 2 outgoing wires.

How many amps are you looking at switching?
I too was a little unclear on the two separate power sources AND two separate loads that can never run at the same time. Can they run at the same time as long as each one is on a different power source? If not, why not? Is this a power issue or is it a safety issue?

Or did you really mean that at all?

A double throw safety switch is simple enough to switch loads so that your power source only feeds one or the other but not both at the same time. The only caveat is to look at the HP rating of the switch, not the Amp rating, they may be different. But then again if you NEVER EVER switch under load, which seems unlikely, then it really wouldn't matter as long as you have the amps covered.
 

Npstewart

Senior Member
I think I understand why you would say it would be more complicated now, its because of the two loads and two sources.

Its kind of a long story why I was asking. We have a wood shop, and if you exceed a certain amount of exhausted cfm then the shop has to comply with nfpa 664. I was trying to come up with a way to have all the machines in the shop that we need, but make it impossible to exceed the cfm by not allowing simultaneous use of the two largest machines. I guess if I drew a wiring diagram of the double throw disconnect method I would have realized the problem.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I too was a little unclear on the two separate power sources AND two separate loads that can never run at the same time. Can they run at the same time as long as each one is on a different power source? If not, why not? Is this a power issue or is it a safety issue?

Or did you really mean that at all?

A double throw safety switch is simple enough to switch loads so that your power source only feeds one or the other but not both at the same time. The only caveat is to look at the HP rating of the switch, not the Amp rating, they may be different. But then again if you NEVER EVER switch under load, which seems unlikely, then it really wouldn't matter as long as you have the amps covered.

Now I see why Jim made his comments. I took the OP to mean one source, two loads. My bad.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I think I understand why you would say it would be more complicated now, its because of the two loads and two sources.

Its kind of a long story why I was asking. We have a wood shop, and if you exceed a certain amount of exhausted cfm then the shop has to comply with nfpa 664. I was trying to come up with a way to have all the machines in the shop that we need, but make it impossible to exceed the cfm by not allowing simultaneous use of the two largest machines. I guess if I drew a wiring diagram of the double throw disconnect method I would have realized the problem.

Interesting problem. I would have solved it with a permissive circuit in each controller from a little PLC that is connected to a CFM transducer. If the CFM transducer says you are at the limit, the PLC disallows starting of any more loads. Then after some trial and data collection, tabulate the loads by CFM requirements and make a truth table in the PLC to allow/disallow different sized machine combinations.

But I'm a controls geek, I know that's not for everyone...
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I think I understand why you would say it would be more complicated now, its because of the two loads and two sources.

Its kind of a long story why I was asking. We have a wood shop, and if you exceed a certain amount of exhausted cfm then the shop has to comply with nfpa 664. I was trying to come up with a way to have all the machines in the shop that we need, but make it impossible to exceed the cfm by not allowing simultaneous use of the two largest machines. I guess if I drew a wiring diagram of the double throw disconnect method I would have realized the problem.

Use two 2-pole contactors with their coils controlled by a standard SPDT switch.

Use a 4-pole double throw switch and only wire to two poles in either position.
 