Hair Dryer Load

Status
Not open for further replies.

KWH

Senior Member
I was curious if anyone has taken a amp reading on a hand held hair dryer, if the watt rating for output comes out the same as if you divided by the voltage. I am doing a beauty salon and figured one dedicated circuit per chair but now there talking about 2300watt dryers.
 
I have never seen an amp reading that matched the nameplate. Well rarely anyway but I haven't checked any hair dyers
 
I was curious if anyone has taken a amp reading on a hand held hair dryer, if the watt rating for output comes out the same as if you divided by the voltage. I am doing a beauty salon and figured one dedicated circuit per chair but now there talking about 2300watt dryers.

I did one not long ago, and ran a seperate circuit (12/2/2) to each receptacle after breaking the tabs. Each receptacle is on a 20 amp double pole breaker.
I also like to do this to bathroom receptacles in houses for the same reason. By the time a hairdryer and a curling iron are pluged up, the receptacle is seeing 3200-4000 watts.
 
it matches so well that our local poco uses it as verification their meteres are accurate. all the feld techs carry a cheap kmart 1000watt hair dryer and show that 1 rev of meter wheel with hair dryer load is 60 seconds. I think this justifies they should be accurate. at least some of the cheap ones.
 
it matches so well that our local poco uses it as verification their meteres are accurate. all the feld techs carry a cheap kmart 1000watt hair dryer and show that 1 rev of meter wheel with hair dryer load is 60 seconds. I think this justifies they should be accurate. at least some of the cheap ones.

We have sometihing like a hairdryer that we test services with, a super beast http://www.arnettindustries.com/pdf/Superbeast.pdf

our meter verification is done with a little more accurate machine though.
 