E electrobuzz Member Location Portland, OR Jun 14, 2012 #1 Is it required to use a current transformer for a 400A meter?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jun 14, 2012 #2 That is a question for your utility. I have seen both self-contained and CT meters for 400 services.
O Open Neutral Senior Member Location Inside the Beltway Occupation Engineer Jun 14, 2012 #3 don_resqcapt19 said: That is a question for your utility. I have seen both self-contained and CT meters for 400 services. Click to expand... PG&E required CT's for 400A service.
H Hv&Lv Senior Member Location - Occupation Engineer/Technician Jun 14, 2012 #5 You need to check to see if your utility has K base meters. If so, buy a K base socket. To answer your question, yes if they don't have K base meters. No if they do have them.