- New Jersey
- Journeyman Electrician (retired)
I would always read that as 3 ungrounded conductors and a grounded conductor.
Me too. The EGC is implied and not specific to the 3 phase, 4 wire phrase.
I agree I was careless however I know horsegoer and I was pretty certain he was not talking about a corner grounded delta.
Even if there is some standard as to how to properly say it, it is not followed consistantly enough throughout the industry.
Example: 120/208 3ph 4 wire - most would assume is 3 phases and a neutral (and it is assumed you always need an equipment ground if on load side of service equipment so there may be a 5th assumed conductor.
Example 208 3 ph 4 wire - most would assume there is no neutral load since the 120 was not mentioned so three phases and an equipment ground.
Example 120/240 3 wire - probably single phase with neutral - equipment ground is needed if on load side of service so 4th wire is assumed.
Example 120/240 3 wire non grounding - kind of the designation for the 3 wire range receptacles where the neutral was allowed to perform equipment grounding also.
You really need to pay attention to other details to hopefully clarify what is needed. If you have a description of loads supplied and there is neutral needed by certain loads you can then figure you need how ever many necessary phases plus the neutral and equipment ground for that load.
That is helpful....so if you know the load like the example below what woud you say the wire configuration is??
277/480 3P 4W panel feeding a 480V 3P 3W panel and they list the feeder as 3#3/0 in 2 1/2" conduit. Do you think there is a missing conductor? Is it just 3 conductors? Thanks.
Does it help clue you in that it is a feeder feeding a panel????
Does the panel supply any 277 volt loads? That is what I would be looking for to determine if a neutral is needed.
If it only supplies 480 volt loads a neutral is not needed but then you have to decide if you or the designer wants one just in case someday 277 loads will be added.
Ok, I'll check but what does the 3W represent..3 hots???? And if it is 3 hots(ungrounded conductors) then you have two questions...the neutral and the EGC....no?
And actually the 277/480 3P 4W panel also feeds a 277/480ZV 3P 4W panel...and still only lists 3 conductors for the feeder??
480V, 3Ph, 3W represents 3-hots + EG
277/480V, 3Ph, 4W represents 3-hots, 1-Nuet + EG
If it only lists 3 conductors, to a 277/480V panel, it could be correct or a mistake.
If you are bidding, you could RFI it or give an add below the line for the correction.
3 wire feeder can be a single phase panel - 2 hots and a neutral- but unlikely. It could also be a straight 3 phase panel where no neutral is needed. I don't see it as a 3 phase panel with neutral.
... 277/480 3P 4W panel also feeds a 277/480ZV 3P 4W panel...?
The correct terminology, per ANSI/IEEE standards, and referenced in the NEC is: 480Y/277V [3Ph 4W is optional] for 3 lines + 1 neutral, ground is not mentioned. but, for some reason many utilites and manufacturers do not follow this terminology.
In my experience grounding conductors are not included in the vast majority of descriptions; the two notable exceptions being cables and wiring devices.
Is this on a set of plans you are bidding?
Are all of the loads in the panel 3Ph/3W? If so, 3 phase conductors will work.
But it may not be the engineer's intent. They may want to pull a neutral for future 277/480V loads.
I see panel schedules all of the time not match the feeder.
Bid as drawn and scheduled and qualify it.
Utilities don't mention EGC because they are rarely dealing with EGC's as they are typically only talking service conductors.
It's a budget...but also want to know about thbis for my own knowledge. I can you tell if all the loads out of the panel that is being fed are 3P3W? What is some are single phase?
I have seen many feeder schedules list the ground wire.
Yes to what Little Bill said. Utilities are not talking feeders they are talking service conductors. Equipment ground and grounded service conductor are essentially same conductor in those cases. Separate conductors is pointless if they are connected together at each end as this makes them parallel and not separate in function.I have seen many feeder schedules list the ground wire.